Honeywell T5, I think I wired it wrong.


bryanduke's Avatar
Member

Join Date: Mar 2017
Posts: 11

03-19-17, 09:42 PM   #1 (permalink)  
Honeywell T5, I think I wired it wrong.

I recently installed a Honeywell T5 at my house. This thing has been working great, UNTIL, I turned on the A/C the other day for the first time. It was still blowing heat. I have tried messing with the settings and reconfiguring the software, but only heat. I did at one point have it to when the A/C was supposed to be on, it was just the fan blowing, no heat, no cool. Here is a photo of the wiring of the original thermostat.
Name:  IMG_20170315_223519.jpg
Views: 269
Size:  38.7 KB
My wiring has both a B wire and an O wire, but does not have a C wire. Here is the T5s wiring.
Name:  IMG_20170317_225934.jpg
Views: 255
Size:  49.5 KB
Here is what I connected to the T5:
Red - R
Black - W2(Aux)
White - W
Yellow - Y
Green - G
Orange - O/B
Blue - C
Brown - Unused on both thermostats and not pictured.

I also have a brown wire that is unused. Any ideas? I had to go back to my original thermostat because it has been getting pretty warm here the past few days and we needed a little A/C.

Here are a few photos of the settings in the installation guide too. I have tried just about every configuration and it still didn't work.
Name:  IMG_20170317_230105.jpg
Views: 215
Size:  33.1 KB
Name:  IMG_20170317_230110.jpg
Views: 207
Size:  29.2 KB

Thank you in advance.

 
Sponsored Links
PJmax's Avatar
Group Moderator

Join Date: Oct 2012
Posts: 38,877
NJ

03-19-17, 10:34 PM   #2 (permalink)  
Welcome to the forums.

We know the wiring on your old stat but we don't know what make and model the old stat is. We know you have a heatpump with backup electric heat.

Red - R .................. R (R switch up)
Black - W2 ............ tape off - not needed
White - W1 ........... W
Yellow - Y1 ............ Y
Green - G ............. G
Orange - O ........... O
Blue - B ............... ?

200- system type - heat pump
205 - equipment type - air to air
218 - reversing valve - O/B on cool
220 - cool stages - 1
221 - heat stage - 1 AUX/E - 1


~ Pete ~

 
bryanduke's Avatar
Member

Join Date: Mar 2017
Posts: 11

03-20-17, 10:38 AM   #3 (permalink)  
It is a Trane unit and the thermostat is also Trane branded. I will check the model number later this evening when I get home.

 
PJmax's Avatar
Group Moderator

Join Date: Oct 2012
Posts: 38,877
NJ

03-20-17, 10:48 AM   #4 (permalink)  
Ok...so then the B is the C connection for your new stat.


~ Pete ~

 
bryanduke's Avatar
Member

Join Date: Mar 2017
Posts: 11

03-20-17, 04:14 PM   #5 (permalink)  
I am pretty sure that is how I had it hooked up, except I did have the W2 hooked up. I will give it another go and see if that makes any difference.

It looks like my old thermostat is a Trane XR402

Here is a photo of the only sticker I could find on the old thermostat.
Name:  IMG_20170320_165423.jpg
Views: 206
Size:  52.1 KB

 
PJmax's Avatar
Group Moderator

Join Date: Oct 2012
Posts: 38,877
NJ

03-20-17, 04:26 PM   #6 (permalink)  
Did you confirm the programming ?

The reversing valve must be powered for cooling. 218 - O on with cool.


~ Pete ~

 
bryanduke's Avatar
Member

Join Date: Mar 2017
Posts: 11

03-20-17, 05:03 PM   #7 (permalink)  
I wired it up and configured it just like described earlier. When I turn it to Cool and it kicks on, now it is blowing room temp air, seems like the compressor is not kicking on. Just 20 minutes ago it was cooling great with the old thermostat connected. Set the t-stat as follows: Heat Pump - Air to air - o/b on cool - cool stage 1 - heat stage - 1 emergency heat 1. Here is a photo of how it is hooked up.
Name:  IMG_20170320_175929.jpg
Views: 362
Size:  38.7 KB

 
PJmax's Avatar
Group Moderator

Join Date: Oct 2012
Posts: 38,877
NJ

03-20-17, 05:10 PM   #8 (permalink)  
Is the R/Rc/Rh switch in the single wire position ?

===============================================

There is not a lot of wide spread tech info on that stat yet. In looking at your wiring in post 7 ...... you may have to move the W wire to W2 OR try connecting the black to W2.

W2 is labeled as AUX which means it needs an electric heat connection to it.


~ Pete ~

 
bryanduke's Avatar
Member

Join Date: Mar 2017
Posts: 11

03-20-17, 05:12 PM   #9 (permalink)  
Yes, it is. I really appreciate all the help you are giving me too. I just don't know what it could be.

 
bryanduke's Avatar
Member

Join Date: Mar 2017
Posts: 11

03-20-17, 05:15 PM   #10 (permalink)  
I don't have a thermometer to check, but it feels like it might be blowing a little cooler than the ambient temp. Could my system possibly be 2 stage cool?
+++++++
I originally had the black wire connected to w2. I will give it a try again.

 
bryanduke's Avatar
Member

Join Date: Mar 2017
Posts: 11

03-20-17, 05:28 PM   #11 (permalink)  
Moved the White wire from W to W2. Blowing cold

I will let it cool back down in here and test to see if the heat works. Hopefully that gets everything going.

Thank you very much.

 
PJmax's Avatar
Group Moderator

Join Date: Oct 2012
Posts: 38,877
NJ

03-20-17, 05:29 PM   #12 (permalink)  
The W wires are only for electric heat. That won't affect the A/C.
The white wire should not have any effect on A/C.

When you turn the stat to cooling.... wait 5 minutes and then go outside and see if the compressor is running. If it is..... then check the larger, insulated refrigerant line. It should get cold.


~ Pete ~

 
bryanduke's Avatar
Member

Join Date: Mar 2017
Posts: 11

03-20-17, 05:39 PM   #13 (permalink)  
I had to wait 5 minutes for the compressor to reset or whatever it does each time I remove the t-stat and change something then put it back on. I was going outside each time and checking the unit, it was running every time, but never cooling. When I moved the white wire from W to W2 and waited 5 minute then it kicked on and started cooling. No clue why. I will try to change it back later and see if it keeps it from cooling again. I found a little thermostat and check it at the return and in a vent before and after I changed the white wire. Before it was the same temp at both places. Now it is cooling about 20 degrees at the vent compared to the return.

 
PJmax's Avatar
Group Moderator

Join Date: Oct 2012
Posts: 38,877
NJ

03-20-17, 05:47 PM   #14 (permalink)  
You may need to investigate further.

The orange O wire is supposed to control the reversing valve. It was connected to the O terminal on the old stat. Power on the valve = cooling. No power on the valve = heating

Pictures of the wiring at the air handler and at the heatpump are helpful.

The stat has a 5 minute compressor delay built in to keep from damaging the compressor from short cycling.


~ Pete ~

 
bryanduke's Avatar
Member

Join Date: Mar 2017
Posts: 11

03-20-17, 05:52 PM   #15 (permalink)  
So open up the panel that has all of the wiring in it and take a photo? My old thermostat also had the 5 minute delay, so i was aware of that. My brother-in-law had his HVAC license a few years ago, but he got into drugs real bad and lost everything. I have helped him install a system before and have basic knowledge of how they work. This thing has just been throwing me for a loop.

 
PJmax's Avatar
Group Moderator

Join Date: Oct 2012
Posts: 38,877
NJ

03-20-17, 05:55 PM   #16 (permalink)  
With pictures I can visually see where the wire are connected.


~ Pete ~

 
bryanduke's Avatar
Member

Join Date: Mar 2017
Posts: 11

03-20-17, 06:15 PM   #17 (permalink)  
Here are a few photos from inside the unit.
Name:  IMG_20170320_185846.jpg
Views: 214
Size:  50.7 KB
Name:  IMG_20170320_185858.jpg
Views: 216
Size:  42.8 KB

 
PJmax's Avatar
Group Moderator

Join Date: Oct 2012
Posts: 38,877
NJ

03-20-17, 06:41 PM   #18 (permalink)  
Bottom picture is good. See if you can pull the wiring out a little so I can see more of the connections.

The brown cable in the front with the unconnected white wire is the outside condensor cable. I need to see the stat cable behind it.


~ Pete ~

 
bryanduke's Avatar
Member

Join Date: Mar 2017
Posts: 11

03-20-17, 06:55 PM   #19 (permalink)  
I changed it over to heat and heat works too. Here are a few photos from different angles.
Name:  IMG_20170320_194703.jpg
Views: 212
Size:  47.5 KB
Name:  IMG_20170320_194753.jpg
Views: 211
Size:  43.2 KB

 
PJmax's Avatar
Group Moderator

Join Date: Oct 2012
Posts: 38,877
NJ

03-20-17, 07:32 PM   #20 (permalink)  
You can see the white and black thermostat wires combined and connected to the common white reheat line.

Single yellow wire..... one stage A/C.
Single white wire..... one stage heating coils.

Name:  diagram x.jpg
Views: 231
Size:  49.6 KB


~ Pete ~

 