Replace Thermostat
I currently have a Trane XL19i with a TH8320U1040 (TCONT802AS32DAA) thermostat. 6 Wires currently coming to the thermostat:
Current Wiring - See picture with wires
Left Side
Black > Y2
Right Side
RC Jumpered to R
R < Red (There is a jumper between RC and R)
O < Orange
Y < Yellow
G < Green
B < Blue

I am looking to replace the thermostat with at Honeywell RTH8500.
What wires go to where?
See blank place picture
I have the Y2 on left, so that one is covered, but on the right I have
RC Jumpered to R
R
O/B
Y
G
C

Also, for system type, they give you 10 options under function 0170.
Page 18
https://customer.honeywell.com/resou.../69-1902EF.pdf
I beleive my system is "10" (Conventional multi-stage system). Is that correct?
Do I need to change anything on settings 0180, 0190, 0240, or 0270?
Current Wiring - See picture with wires
Left Side
Black > Y2
Right Side
RC Jumpered to R
R < Red (There is a jumper between RC and R)
O < Orange
Y < Yellow
G < Green
B < Blue

I am looking to replace the thermostat with at Honeywell RTH8500.
What wires go to where?
See blank place picture
I have the Y2 on left, so that one is covered, but on the right I have
RC Jumpered to R
R
O/B
Y
G
C

Also, for system type, they give you 10 options under function 0170.
Page 18
https://customer.honeywell.com/resou.../69-1902EF.pdf
I beleive my system is "10" (Conventional multi-stage system). Is that correct?
Do I need to change anything on settings 0180, 0190, 0240, or 0270?
Last edited by PJmax; 10-09-17 at 01:19 PM. Reason: pictures
#2
This should do it.
Red - Rc jumpered to R
Orange - W
Yellow - Y
Green - G
Blue - C
Black - Y2
170 ----> 10
180 ----> 0
240 ----> 5
Red - Rc jumpered to R
Orange - W
Yellow - Y
Green - G
Blue - C
Black - Y2
170 ----> 10
180 ----> 0
240 ----> 5