Question Carrier 50QE900-NPWS Wiring with BOW together

Hello,
I'm attempting to replace my current non-programmable thermostat with a new Honeywell RTH6360. When I pulled the older Carrier off, I documented the wiring per instructions with a blue wire going to a slot labeled BOW1, but when plugging in the new UWP, I saw B/O and W were separate. I've tried plugging into each and neither kicks on the heat. Do I potentially need a jumper or something?

Name:  t1.jpg
Views: 622
Size:  55.8 KB

Name:  t1a.jpg
Views: 2612
Size:  70.8 KB
 

Last edited by PJmax; 04-19-18 at 03:22 PM. Reason: reoriented pics
  #2  
Old 04-19-18, 01:29 PM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
Jumper between O/B and W.
 
  #3  
Old 04-19-18, 03:25 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,816
Received 3,922 Upvotes on 3,518 Posts
Welcome to the forums.

It's W or B/O function depending if you have a heat pump or a split A/C system and furnace.

On the new stat.....
If you have a furnace and split A/C..... you use W.
If you have a heat pump system.... you use O/B.

If you have a Ruud or Rheem heat pump..... you'd need to change the O/B programming to B. O is the normal default setting.
 
 