Nest Install Help

I need wiring help connecting a Nest thermostat to a Rudd heat pump outdoor unit Model: UPQL-030JEZ. Current thermostat is Honeywell TH4210D1005. t-stat wiring is E-AUX Jumped, Y, G, O, R, B, C. L is not in use.

According to the Nest compatibility checker my system is not compatible. I suspect it has to do with my unit using separate signals for the changeover valve for heating and cooling. Is there a workaround for this or am I out of luck.

Thank you for reading.
 
  #2  
Old 12-01-18, 07:59 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,017
Received 3,407 Upvotes on 3,057 Posts
Welcome to the forums.

Can you post a picture of the thermostat wiring ? ........ How-to-insert-pictures

It's rare to see a wire in both the O and B terminals unless you have an air zoning system.
 
  #3  
Old 12-01-18, 08:15 AM
J
Member
Thread Starter
Join Date: Nov 2018
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Here you go. Thanks for responding so quickly!

I do not have air zoning.

Justin
 
Attached Images  
  #4  
Old 12-01-18, 08:32 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,017
Received 3,407 Upvotes on 3,057 Posts
Thanks.

A Rheem/Ruud unit uses the B connection for changeover..... not O.
That Ruud condenser has diagnostics that are sent out on the L wire. I have a feeling your current thermostat was wired incorrectly and the orange wire was on L on the original stat and should not have been used on the current or new thermostat.

The only way to confirm this is to check the wiring connections at the outside condenser and the air handler. You could also temporarily remove the orange wire and see if the system works in heat and cooling modes.

Typical connections shown on page 18 of manual
Ruud manual
 
  #5  
Old 12-01-18, 10:08 AM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,471
Received 83 Upvotes on 75 Posts
Sometimes you need both O and B if you have a zoned system - multiple thermostats connecting to a zone control board. Verify that is not the case.
 
  #6  
Old 12-01-18, 10:13 AM
J
Member
Thread Starter
Join Date: Nov 2018
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
You are correct, I removed the orange wire from the O terminal and both heating and cooling are working correctly.

Thanks for explaining everything so clearly and linking the manual. I installed the new t-stat successfully.

You are a great resource for this community, thanks again.

Justin
 
  #7  
Old 12-01-18, 11:17 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,017
Received 3,407 Upvotes on 3,057 Posts
Thanks A..... I had mentioned a zoning system and he said it wasn't.
 
  #8  
Old 12-01-18, 12:20 PM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,471
Received 83 Upvotes on 75 Posts
Some don't know the term zoning but do understand multiple thermostats. Not always the same thing but close enough.
 
 