Installing an ecobee3 lite with no C

Hi,

According to the compatibility checker it told me it would work but I would need to use the included power extender kit. When it arrived I followed the instructions except I'm using it on a gas boiler for heat only and I don't see the connections that the extender kit is looking for.

I've spent a bit of time with ecobee support and they told me I need to find where the wires from the thermostat are connected to at the boiler. So far I've had no luck :-(

Here's a pic of my current thermostat, the wires are in the Rh, Rc, Y, G and W slots:


Here's a pic of the zone controller:


And here's pics of the honeywell aquastat:



Thanks in advance for any and all help!!
 
Sponsored Links
  #2  
Old 04-17-19, 09:00 AM
Member
Join Date: Jun 2012
Location: USA
Posts: 1,325
Likes Received: 1
You are looking in the wrong place. You don't need a C from the boiler but from the air handler. See https://support.ecobee.com/hc/en-us/...iring-Diagrams
Also - don't use W with the PEK as you have a boiler.
PEK officially doesn't work with two transformers (Rc and Rh wires)
https://support.ecobee.com/hc/en-us/...former-system-
 
  #3  
Old 04-17-19, 09:06 AM
Member
Thread Starter
Join Date: Apr 2019
Location: United States
Posts: 6
Thanks, but this is for baseboard radiators not forced air.
 
  #4  
Old 04-17-19, 09:10 AM
Member
Join Date: Jun 2012
Location: USA
Posts: 1,325
Likes Received: 1
The Rc, Y, and G are normally for air conditioning (forced air). Rh and W can be for any type of separate heating system.
 
  #5  
Old 04-17-19, 09:19 AM
Member
Thread Starter
Join Date: Apr 2019
Location: United States
Posts: 6
Could it be that I don't even need the Rc, Y, and G wires at all and I really only have 2 wires in use?
 
  #6  
Old 04-17-19, 09:39 AM
Member
Join Date: Jun 2012
Location: USA
Posts: 1,325
Likes Received: 1
Heat only uses Rh and W which should go to the ARM zone board terminals Tr and Tw (yours look reversed). C would be the "COMMON" terminal on the right. Problem is a thermostat with Rc and Rh won't work properly with a C sourced from the same system as Rh.

It looks like the Rc,Y, and G are a different wire type - most likely going to an air handler for air conditioning. If you don't have that you can disconnect them and tape off.
 
  #7  
Old 04-17-19, 09:50 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 50,200
Likes Received: 82
The old two wires currently connected to Rh and W look to be heavier like #14. That may have been a 120v thermostat originally and was converted.

Does that stat control A/C ?
What zone on the zone board is it ?
 
  #8  
Old 04-17-19, 09:55 AM
Member
Thread Starter
Join Date: Apr 2019
Location: United States
Posts: 6
Yes, the Rh and W are a bit thicker then the others. It does not control A/C it's only for the baseboard heat, I have a separate stat for A/C.

I *think* it's zone 2.
 
  #9  
Old 04-17-19, 10:10 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 50,200
Likes Received: 82
There is a three wire connected to zone two. I'd follow that cable and see if you can find a splice to those heavier wires. You can get a C connection from that controller but you need three wires. Maybe you can find that multi wire cable that is currently on the stat in the basement.
 
  #10  
Old 04-30-19, 06:49 PM
Member
Thread Starter
Join Date: Apr 2019
Location: United States
Posts: 6
Is there any reason I can't/shouldn't just use a plug in transformer? I'm pretty sure I can have the wire behind the wall so it's not unsightly.
 
  #11  
Old 04-30-19, 07:01 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 50,200
Likes Received: 82
If you're running wire in the wall..... just pull in the correct wire.
Otherwise..... yes..... you can use a plug in 24vAC transformer.
 
  #12  
Old 04-30-19, 07:06 PM
Member
Thread Starter
Join Date: Apr 2019
Location: United States
Posts: 6
Thanks, I meant I can get the wire from an outlet to the stat behind the wall not that I'm running a wire.

Which plug in transformer do you recommend?
 
  #13  
Old 04-30-19, 08:12 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 50,200
Likes Received: 82
Here's a page of them at Amazon...... 24 vac wall warts
They come in white and black with color coordinated wiring.
 