American Standard Conversion to Hunter

Reply

  #1  
Old 08-03-19, 02:18 PM
Member
Thread Starter
Join Date: Aug 2019
Posts: 3
Upvotes: 0
Received 0 Votes on 0 Posts
American Standard Conversion to Hunter

I have an old America Standard thermostat and am trying to move it to a hunter.

According to the directions, I am left with T, X2, and B wires that do not connect to the Hunter System.

I have a heat pump with Aux. heat.

American Stand. (AS)
R=red
T=brown
O=orange
G=green
Y=yellow
X2=black
B=blue
W=white
F has no wire to it.

Hunter-General conversion (Hunter=AS)
R=R
Y=Y
E=W
blank = X2
0=0
B= blank
G=G
L= blank

On the Hunter directions for Single Stage Heat Pump w/Aux.Heat the following are the wires to hook up.
R=R
Y=Y
G=G
O=O
Aux/E=E (the white wire from America Standard, not the black from AS)

I am left with T, X2, and B from the AS key going to nothing and have taped them off with electrical tape.
Model #
America Standard AYSTAT655
Hunter 44133

I have it connected now and have taped off the three wires listed above. It is running, I have not programmed it and have not run the heat (in FL,too hot).

Please let me know if I have done this correctly.

Thank you!!!
 

Last edited by ChristyGibbons; 08-03-19 at 03:10 PM.
Sponsored Links
  #2  
Old 08-03-19, 02:36 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 51,486
Received 216 Votes on 205 Posts
Welcome to the forums.

C=C
What does this mean ?

Your American Standard B connection is the system common.
If your new thermostat requires a C connection..... then it's blue.
If it doesn't need a C connection.... tape it off.
 
  #3  
Old 08-03-19, 03:13 PM
Member
Thread Starter
Join Date: Aug 2019
Posts: 3
Upvotes: 0
Received 0 Votes on 0 Posts
Thanks Pete,
The C=C was G=G, I fixed it.

It is okay to connect the O and the B? I have both wires and Hunter has both options on the connector, but does not show to connect the B for a Single Stage Heat Pump w/Aux. Heat, only the O.

Thanks again and for a quick response.
 
  #4  
Old 08-03-19, 04:42 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 51,486
Received 216 Votes on 205 Posts
NO..... you connect the O only.
If that is a battery thermostat..... tape off the blue wire.
 
  #5  
Old 08-03-19, 05:33 PM
Member
Thread Starter
Join Date: Aug 2019
Posts: 3
Upvotes: 0
Received 0 Votes on 0 Posts
Thank you so much, Pete!!!!
 