Can I use DHW Aquastat line as constant 24V C to power Smart T-stat?

Can I use DHW Aquastat line as constant 24V C to power Smart T-stat?

Reply

  #1  
Old 08-25-19, 09:37 AM
Member
Thread Starter
Join Date: Aug 2019
Posts: 2
Received 0 Votes on 0 Posts
Can I use DHW Aquastat line as constant 24V C to power Smart T-stat?

Hi - new to the site, so apologies if this is a dumb question (or a repeat, however I looked and couldnít find this exact question) but...I have a Weil-McLain Gold CGa boiler with 2 zones heating my baseboards. I also have 2 nest thermostats, which have recently been losing battery power after a recent upgrade. I have both Rh and Rc connected (we have independent air conditioner units), however the nest is only recognizing the Rc connections. Iíve done enough research to know I need to connect a constant 24V C from the boiler unit (Rh line).

However, the Weil-McLain doesnít seem to have stand along ports I can run the C line too (the Blue wire runs to my basement, but its cut off so I just need to connect it). However, I do have an unused Aquastat power line + constant (what I believe to be constant anyway) and was wondering if I could use that as my C line? Iíve been studying the wiring on this, and know the lines from the transformer runs into the unit via connector, and then there is a t-stat output connector which currently has a t-stat neutral line (black), a hot line (also Black but split three ways: to T-stat (black), to unused DHW Aquastat (blue capped line), and to Guard Dog Low Water Cut Off (red)), a ground (green), another neutral (black - going to guarddog LWCO) and what I believe is a constant wire for the DHW aquastat (blue wire) I attached pictures of the wiring diagram on the boiler itself and how its wired, trying to show all the above.

Iím obviously not a professional, so just wanted to A) see if my above understanding is correct; B) if I am correct on the wiring, will it work if I use the the DHW constant as my T-stat constant ; and C) make sure this wonít be unsafe for my boiler.

Thanks in advance
 
Attached Images        
Sponsored Links
  #2  
Old 08-25-19, 11:49 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 53,245
Received 381 Votes on 358 Posts
Without looking at all your stuff...... the C connection on any wifi thermostat is referenced to the cooling system. That means the C must come from the A/C system as well as Rc.
 
  #3  
Old 08-25-19, 01:06 PM
Member
Thread Starter
Join Date: Aug 2019
Posts: 2
Received 0 Votes on 0 Posts
That solves that, thanks for the quick reply. Will start over up at the air handlers and see what I have.

Thanks again, appreciate it
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: