Switching to GLAS thermostat
Most of this is pretty cut and dry, but there is some difference in labels on the 2 Tstats.
in FL ac unit outside w air handler and electric heat
I assume Y = Y1
R = R1 ?
The old tstat has an O/B wire, the new has an Aux is this the correct on to use on the new?
Old is Honeywell th6220u2000
new is Glas
in FL ac unit outside w air handler and electric heat
I assume Y = Y1
R = R1 ?
The old tstat has an O/B wire, the new has an Aux is this the correct on to use on the new?
Old is Honeywell th6220u2000
new is Glas
Last edited by 04detroitls; 10-05-19 at 05:02 PM.
#3
Please post a picture of the old wired thermostat base.
R does not = R1...... R would be Rc.
O/B = O
R does not = R1...... R would be Rc.
O/B = O
#4
Member
Thread Starter
Join Date: Aug 2019
Posts: 11
Upvotes: 0
Received 0 Upvotes
on
0 Posts
#6
It's not W2...... it's AUX. You use the inside labeling for a heat pump.
So on your new stat..... what was W2/AUX will now be W1 on the Glas.
So on your new stat..... what was W2/AUX will now be W1 on the Glas.