Nest 3rd Gen to control Carlin burner


  #1  
Old 11-19-19, 11:01 AM
B
Member
Thread Starter
Join Date: Nov 2019
Posts: 1
Received 0 Votes on 0 Posts
Nest 3rd Gen to control Carlin burner

I would like to disconnect older "Blue" Heat-Timer EPU-60 CH and start to control the boiler with 3rd gen Nest ( which is already connected to run AC system) after doing some research I came up with the diagram but I would like to double check if this configuration would work properly:

Name:  tt3.jpg
Views: 60
Size:  121.1 KB

Name:  tt2.jpg
Views: 52
Size:  86.3 KB

Name:  tt.jpg
Views: 60
Size:  57.4 KB
 

Last edited by PJmax; 11-19-19 at 05:15 PM. Reason: resized pictures/labeled diagram
  #2  
Old 11-19-19, 05:16 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 62,628
Received 1,610 Votes on 1,482 Posts
Welcome to the forums.

The connection to power the nest comes from the C terminal which must come from the A/C system.
Eliminate the connection from your second transformer to C.
 
 