New RTH6360 not heating
I picked up the above mentioned thermostat when I saw a deal on it, because I've really wanted a programmable thermostat, but it appears I mixed something up somewhere.
The pictures below are of the old and new wiring. The color coding might be off a bit, the wiring from an old unit was reused, I believe.
Attachment 112720
In the old picture, it's hard to tell, but R and Rc are jumped using what looks like a staple.
Attachment 112721
The heating unit is a Rheem model RQNJ-A036JK.
I tried most of the option combinations, but the last one was:
Heating system type: 2 Heat pump
Heating equipment type: 7 Air to air heat pump
Reversing valve O/B: 0 O/B in cool
Cooling stages: 1
Heating stages: 1
Any help you can provide would be tremendosly appreciated.
The pictures below are of the old and new wiring. The color coding might be off a bit, the wiring from an old unit was reused, I believe.
Attachment 112720
In the old picture, it's hard to tell, but R and Rc are jumped using what looks like a staple.
Attachment 112721
The heating unit is a Rheem model RQNJ-A036JK.
I tried most of the option combinations, but the last one was:
Heating system type: 2 Heat pump
Heating equipment type: 7 Air to air heat pump
Reversing valve O/B: 0 O/B in cool
Cooling stages: 1
Heating stages: 1
Any help you can provide would be tremendosly appreciated.
#4
Rheem, unlike most other manufacturers, powers the reversing valve to heat. The O/B should be set to "B" (energize to heat). It also appears that you have 2 stages of heat & one of cool.
Use a volt meter set for AC volts to check for 24-28 volts between the red & black wires.
Use a volt meter set for AC volts to check for 24-28 volts between the red & black wires.
#6
Your wiring looks OK. Try configuring the stat as I suggest in the previous post. I think you can install batteries & configure the stat before mounting it to the base.
#8
These should be your settings. The thermostat will eventually bring on the AUX heat but it may not be as soon as you increase the thermostat. Have not found a RTH6379D in the list.
200 = 2 (heat pump)
205 = 7 (air to air heat pump)
218 = 1 (O/B in heat mode) This is the correct setting for Rheem/Ruud systems
220 = 1 (cool stage)
221 = 1 (heat stage) 1 (backup heat stage)
200 = 2 (heat pump)
205 = 7 (air to air heat pump)
218 = 1 (O/B in heat mode) This is the correct setting for Rheem/Ruud systems
220 = 1 (cool stage)
221 = 1 (heat stage) 1 (backup heat stage)
JOB voted this post useful.