Picking the right thermostat.

Morning, I just moved into a new house and am looking at getting a smart thermostat. I grew up in a house with just oil heating and AC's in the rooms so a swap was easy, but now I have a CA system as well as oil. I just want to make sure I buy the right thermostat and know if I need to run a C cable. Here's what the guts of the older one look like.
 
Attached Images   
Sponsored Links
  #2  
Old 01-26-20, 11:10 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,635
Received 515 Votes on 485 Posts
Welcome to the forums.

You have two systems controlled by that thermostat. Two distinct cables.
Cable 1............... The heat is on red(Rh) and white(W).
Cable 2............... The A/C is on red(Rc), green(G) and white(W).

You absolutely need a C connection and it comes from the A/C air handler.
Check and see if there are any cut off wires in the A/C cable.
 
  #3  
Old 01-26-20, 04:39 PM
Member
Thread Starter
Join Date: Jan 2020
Posts: 14
Received 0 Votes on 0 Posts
Thanks for clearing that up for me. As far as wires around the AC unit I couldn't find anything that looked cut or out of place. It seems everything is hooked up right.
 
Attached Images  
  #4  
Old 01-26-20, 04:50 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,635
Received 515 Votes on 485 Posts
You have two options.....
1) run a new cable down to the stat. (recommended)
2) you can lose control of the blower at the thermostat and use the fan wire as the C wire.
With this method.... there is no more "FAN ON" mode.
 
  #5  
Old 01-26-20, 06:04 PM
Member
Thread Starter
Join Date: Jan 2020
Posts: 14
Received 0 Votes on 0 Posts
Sounds good, sorry if the info I was giving wasn't nearly helpful enough. By oil heating I mean that I have furnace and baseboard heating. And the cooling is a Goodman A24-00. You wouldn't happen to have a link to a wiring diagram so I can put that C wire in properly?
 
  #6  
Old 01-26-20, 08:25 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,418
Received 14 Votes on 11 Posts
C is the big light gray wire under your thumb in the picture that you posted.

The AC condenser connects to stat Y and air handler C so you will end up with 2 wires connected to the air handler C.
 
  #7  
Old 01-26-20, 09:19 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,635
Received 515 Votes on 485 Posts
You have a boiler and baseboard heat..... A furnace is hot air. A boiler is hot water.
 
  #8  
Old 01-27-20, 06:14 AM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 14,092
Received 16 Votes on 14 Posts
You have just one thermostat for heat? No others in other parts of the house?
 
  #9  
Old 01-27-20, 04:56 PM
Member
Thread Starter
Join Date: Jan 2020
Posts: 14
Received 0 Votes on 0 Posts
It's a ranch so there's just the one.
 
  #10  
Old 01-27-20, 05:13 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,635
Received 515 Votes on 485 Posts
So have we helped you make a decision ?
Any more questions ?
The Ecobee 3 is a good choice...... Honeywell T6 is another.
 
  #11  
Old 01-27-20, 05:27 PM
Member
Thread Starter
Join Date: Jan 2020
Posts: 14
Received 0 Votes on 0 Posts
Yeah you guys have been a great help thanks a ton. I was looking at the ecobee3 before I took to the forums so I'll go with that and hopefully not blow up the house in the process
 
  #12  
Old 01-30-20, 05:32 PM
Member
Thread Starter
Join Date: Jan 2020
Posts: 14
Received 0 Votes on 0 Posts
Went about as well as expected. Any idea where I can attach a C cable?
 
Attached Images  
  #13  
Old 01-30-20, 06:20 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,635
Received 515 Votes on 485 Posts
In your picture in post 3...... that white/gray wire in your thumb is C. You can connect right there.
 
  #14  
Old 01-30-20, 07:09 PM
Member
Thread Starter
Join Date: Jan 2020
Posts: 14
Received 0 Votes on 0 Posts
Tried that, didn't give any juice to the stat.
 
  #15  
Old 01-30-20, 07:32 PM
Member
Thread Starter
Join Date: Jan 2020
Posts: 14
Received 0 Votes on 0 Posts
Forget I wrote that. So I can add a third wire to where the gray and white twist together? Or is one of the white cables coming out of the wall supposed to be C?
 
  #16  
Old 01-30-20, 08:59 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,635
Received 515 Votes on 485 Posts
Name:  w.jpg
Views: 17
Size:  85.4 KB

In your picture..... there is a three wire cable. This cable goes to the stat. If it's still being used..... R (red) goes to orange color. G (green) goes to yellow and white goes to red of the A/C condenser.

How did you get C to the stat ? One wire.... new cable... ?
 

Last edited by PJmax; 01-31-20 at 04:37 PM.
  #17  
Old 01-31-20, 04:09 PM
Member
Thread Starter
Join Date: Jan 2020
Posts: 14
Received 0 Votes on 0 Posts
I used the white wire that's connected to the thick grey cable, because from what I understood was that since it was connected to the grey cable, it would act as a C. But obviously that didn't work. So can I just add a third cable to the grey cable and white wire twist and use that as my C? As I was going over the ecobee instructions it seems that the main issue I'm coming up with is that I have a dual transformer system. I just can't figure out where the C wire is supposed to start at the A/C.
 
  #18  
Old 01-31-20, 04:18 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,635
Received 515 Votes on 485 Posts
Ok..... let's just take a step back. From what you've said and what I see in your pictures you have three wires between the air handler and the thermostat. You need a fourth wire.

How are you going to get a 4th wire to the thermostat ?
 
  #19  
Old 01-31-20, 04:26 PM
Member
Thread Starter
Join Date: Jan 2020
Posts: 14
Received 0 Votes on 0 Posts
I was planning on snaking it from the hole in the wall to wherever the C needs to start from. I know easier said than done, but that's the plan. I've run ethernet cable through the house so I know it's a pain but doable.
 
  #20  
Old 01-31-20, 04:33 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,635
Received 515 Votes on 485 Posts
Ok.... so that wire you are going to run connects to the C of the thermostat and the gray wire at the air handler.
 
  #21  
Old 01-31-20, 04:35 PM
Member
Thread Starter
Join Date: Jan 2020
Posts: 14
Received 0 Votes on 0 Posts
Ok, so just add a third wire to the twist cap at the end of the grey wire and pop the other end in C, that sound right?
 
  #22  
Old 01-31-20, 04:38 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,635
Received 515 Votes on 485 Posts
Yes..... that is exactly correct.
 
  #23  
Old 01-31-20, 04:55 PM
Member
Thread Starter
Join Date: Jan 2020
Posts: 14
Received 0 Votes on 0 Posts
Thanks for being so patient with me on this lol. I'll let ya know how it goes.
 
  #24  
Old 01-31-20, 05:03 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,635
Received 515 Votes on 485 Posts
Not a problem. ......................
 
  #25  
Old 01-31-20, 07:25 PM
Member
Thread Starter
Join Date: Jan 2020
Posts: 14
Received 0 Votes on 0 Posts
Sweet victory. Again, thanks a lot!
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: