Keeping Nest thermostat powered with integrated control

Reply

  #1  
Old 06-20-20, 01:05 PM
M
Member
Thread Starter
Join Date: Jun 2020
Posts: 1
Received 0 Votes on 0 Posts
Keeping Nest thermostat powered with integrated control

My Nest thermostat is powered by the R and W wires, however I recently had a Mitsubishi integrated control (PAC-WHS01HC-E) installed which essentially opens the circuit for the W wire until the outside temperature falls below a certain temperature. However, in doing this it also means my Nest thermostat just shows a "no power" signal during much of the year. Short of running a common wire to the thermostat is there any way to accomplish this?
 
  #2  
Old 06-20-20, 05:16 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 60,786
Received 1,324 Votes on 1,224 Posts
Welcome to the forums.

Unfortunately in your application you will need a C connection.
You could also use a wall wart somewhere near the nest to supply it with 24vac power.
In the link below are some examples.
24vAC wall wart
 
 