Upgraded from Honeywell to Honeywell thermostat

So the up button didn't want to work unless you really smushed it and wiggled it around. So I bought a new one. I hooked it up about 3 months ago but now the heat doesn't blow any heat, just cold.
Here is the old one.




So I put up the new one wiring it like the manual says for a 1h/1c heatpump.


It worked great all summer for the a/c.
Here is a link to the manual. https://digitalassets.resideo.com/da...3-00181EFS.pdf
 

Last edited by PJmax; 10-16-20 at 03:42 PM. Reason: cropped/resized pics
Sponsored Links
  #2  
Old 10-16-20, 03:11 PM
F
Member
Thread Starter
Join Date: Oct 2020
Posts: 4
Received 0 Votes on 0 Posts
Oh here is how I have it wired to new thermostat.
 

Last edited by PJmax; 10-16-20 at 03:44 PM. Reason: cropped/resized pic
  #3  
Old 10-16-20, 03:50 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,077
Received 1,110 Votes on 1,030 Posts
Welcome to the forums.

Your wiring is ok.
Most of the default program settings are ok.
You must change the following three for your system.

200 = 2 - heat pump
205 = 7 - Air to air heat pump
218 = 1 - B (O/B in heat)

 
  #4  
Old 10-16-20, 04:22 PM
F
Member
Thread Starter
Join Date: Oct 2020
Posts: 4
Received 0 Votes on 0 Posts
Thank you for your reply. I was sure I already had that set correctly, but I went and wrote down all my settings to be sure.
120-2
125-0
200-2
205-7
218-1
220-1
221-1
300-0
340-10
350-0
365-3
375-9
387-2
425-0
430-60
431-80
435-0
702-1
711-6
1400-0
1410-12
1415-1
1420-0
 
  #5  
Old 10-16-20, 04:48 PM
F
Member
Thread Starter
Join Date: Oct 2020
Posts: 4
Received 0 Votes on 0 Posts
Don't know if this helps but the Heat pump is a Rheem.

 
  #6  
Old 10-16-20, 05:26 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,077
Received 1,110 Votes on 1,030 Posts
Your settings look ok.

The O/B supplies power to the reversing valve. The majority of the companies use O for cooling. That means the valve is powered to cool. Rheem and Ruud are two companies that use B for heating. That means the valve is powered to heat. Just the opposite of everyone else.

If I was checking your system.... in heating mode.... I'd go out to the condenser and check from the blue wire to the C wire. You should see 24vAC there. If you do see it there.... it could be a defective reversing valve coil (open) or a problem with the defrost control board inside the condenser.

Do you get heat in emergency mode ?
That would shut down the compressor and use the electric reheats.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: