Nest power adapter and Taco zone valves


  #1  
Old 05-24-22, 08:10 PM
J
Member
Thread Starter
Join Date: May 2022
Posts: 2
Received 0 Votes on 0 Posts
Nest power adapter and Taco zone valves

Hi, I am planning to install the Nest Power Adapter to solve my low power problem on one of my Nest 3rd gen tstat. My hvac system has a total of 4 zones. 2 zones are Heat only, the other 2 zones are Heat & ac. I have 4 of the Nest tstats, but only one is having the low power problem, currently.

I do not see instructions for wiring the device into the Taco valve. I will try to attach a picture of the valve wiring and appreciate if anyone can assist.

The Nest tstat that has the low power problem is the Dining Room. Iím trying to wire the Nest Power Adapter for this zone.
 
  #2  
Old 05-25-22, 09:58 AM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,790
Received 79 Votes on 71 Posts
The dining room valve is driven by a green wire that comes from a cable with red and white. This means that there is a splice upstream that you need to find and would likely be where the Nest Power Adapter needs installed. Find that and provide pics.
 
  #3  
Old 05-25-22, 10:45 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 70,055
Received 2,952 Votes on 2,664 Posts
It looks like the dining room thermostat comes in on green and white. Red is cut off.

If that is correct.................
Disconnect the white wire from R connection and green from ZV terminal 1.
Connect these two wires to the dark gray nest adapters wires. No polarity here.

Connect light gray adapter wire R to R splice.
Connect light gray adapter wire W to terminal 1 on ZV.
Connect light gray adapter wire C to terminal 2 on ZV.
 
  #4  
Old 05-30-22, 07:03 AM
J
Member
Thread Starter
Join Date: May 2022
Posts: 2
Received 0 Votes on 0 Posts
Thank you PJmax. After confirming the tstat white and green wires, I wired in the power connector as you suggested. However Iím seeing only 3.6V (which I think is too low) but it is 40mA (which I believe is good). The tstat is offline, saying low power.

I measured the green and white (heat wired) at the tstat with a multimeter, and it is 24V. This dining room tstat controls both Heat and ac. I also measured the ac wires and it is 26V




Thanks
 
  #5  
Old 05-30-22, 02:55 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 70,055
Received 2,952 Votes on 2,664 Posts
You didn't mention anything about A/C
When both are connected the thermostat power needs to come from the A/C.
 
 