Wire Question

My thermostat has no C wire. My air handler and compressor outside need the C connection. I have extra wires in my thermostat line. Is there a way to connect one to the thermostat and make it work? Or should I just look for another thermostat? This is just a cool only set up.
thank you,
Joe
 
  #2  
Old 06-05-23, 04:37 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,816
Received 3,922 Upvotes on 3,518 Posts
Post some pictures of the wiring at the air handler....... How to insert pictures.

If you want to try and find C yourself..... locate the thermostat cable at the air handler. It will be much larger than the condenser cable. The Y- yellow wire in the T'stat cable should go to one of the condenser wires. The other condenser wire will be connected to C.
 
  #3  
Old 06-05-23, 04:48 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,319
Received 874 Upvotes on 737 Posts
The common typically originates from the air handler or furnace. You should find it there on the main board.
 
  #4  
Old 06-05-23, 05:52 PM
J
Member
Thread Starter
Join Date: Aug 2002
Location: Pennsylvania
Posts: 110
Upvotes: 0
Received 0 Upvotes on 0 Posts
Yes, I do see the C in the air handler and the C wire in the Condenser, however theres nothing in the thermostat. The diagram shows thet i need to connect the C in the thermostat (which theres no terminal for) to the C in the air handler, then on to the C in the condenser. Seems to me I'd have no control from the thermostat to turn on the condenser. I talked to a rep for white rogers and he said I didn't need a C because the thermostat uses batteries.
Who knows,lol, I'm stumped
I'll ger some pic up on here.
 
  #5  
Old 06-05-23, 06:25 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,319
Received 874 Upvotes on 737 Posts
The only reason you need a C wire to the thermostat is if it needs to be powered with 24 volts. If it has or can run on batteries then you do not need to connect the C wire to the thermostat.

Note: It is often required to connect a C wire to a NEST thermostat or other smart thermostat.
 
  #6  
Old 06-05-23, 07:26 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,816
Received 3,922 Upvotes on 3,518 Posts
Most battery powered thermostats don't require a C connection.
The C connection is to operate the display on some stats as well as the wifi section if a smart stat.
 
  #7  
Old 06-06-23, 01:58 AM
J
Member
Thread Starter
Join Date: Aug 2002
Location: Pennsylvania
Posts: 110
Upvotes: 0
Received 0 Upvotes on 0 Posts
Yeah, I got that, so...my C terminal on the air handler should connect to the condenser outside and i should be good.

thermostat nc air handler ---------C----------condenser
 
  #8  
Old 06-06-23, 07:03 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,319
Received 874 Upvotes on 737 Posts
Yes, and you also run the Y wire from the stat to the air handler and from the air handler to the other side of the condenser relay coil.
 