Is The Floor Strong Enough?
Received 0 Votes
I am remodeling my two small second story bathrooms(160 sq ft,) by removing flooring and drywall and adding marble and natual stone. The stone weighs about 9lbs per square ft which will be added to the floor and walls. I am concerned about the weight. The floor consists of 2x10s on 16" center with a span of 13ft. The flooring wll consist of 3/4 inch plywood and 1/4 inch durrock.
Is the floor stron enough to support the added weight?
Thanks.
KK
Thanks.
KK
Received 0 Votes
Thanks.
KK
Thanks.
KK
Kay - Your not fine for natural stone. You don't come close to L720 at 13'. You need to either shorten that span by supporting it from below or possibly sistering the floor joists. You do need a second layer of plywood (at least 1/2") for natural stone. Adding the plywood helps with deflection between the joists, but does not help with deflection along the length of the joists.
Doug - where are you coming up with - yep your fine?
I hope Kay comes back to look at this cause shes not fine.
Received 0 Votes