Thermal Expansion With Pressure Valve
#1
Thermal Expansion With Pressure Valve
I had a pressure-reducer installed (line pressure was 100 psi). Now I seem to be getting pressurization from thermal expansion of the water heater backing up into what is now a closed system. I assume there's some straightforward solution - can someone explain what it might be and how it works? Thanks.
#2
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 17,505
Upvotes: 0
Received 1 Upvote
on
1 Post

You can put a bladder expansion tank anywhere in the home on the water line cold or hot. This should take care of it for you. I see that some citys call for them now if you have a backflow check in the water line.
ED
ED

#3
An expansion tank will solve problem.
PRV should have intregal bypass built in to allow back pressure to be relieved. Pressure reducing valve is different than backflow preventer which creates closed system.
PRV should have intregal bypass built in to allow back pressure to be relieved. Pressure reducing valve is different than backflow preventer which creates closed system.
#4
www.wattsreg.com
Click on products, then thermal expansion.
Make sure when you install an expansion tank that you precharged the tank to the setting of PRV FIRST, and without water in the tank. The expansion tank should be installed between the top of the tank and the shut off valve, the location where thermal expansion is most common.
Click on products, then thermal expansion.
Make sure when you install an expansion tank that you precharged the tank to the setting of PRV FIRST, and without water in the tank. The expansion tank should be installed between the top of the tank and the shut off valve, the location where thermal expansion is most common.