Surface ignitor won't light automatically


  #1  
Old 08-29-08, 06:30 AM
P
Member
Thread Starter
Join Date: Aug 2008
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Surface ignitor won't light automatically

I have a Richmond Powervent gas water heater. It has a hot surface ignitor. When the water cools (either from time or use) to where it should ignite, it doesn't. The water heater begins running but no glow from the ignitor.

If I turn the ignitor off and then back on manually, it DOES beginning glowing, and it fires up. It stays lit until the water is completely heated so I wouldn't think it's the themocoupler.

Any thoughts?
 
  #2  
Old 08-29-08, 03:10 PM
H
Member
Join Date: Jul 2005
Location: New York
Posts: 657
Upvotes: 0
Received 0 Upvotes on 0 Posts
My suspicions is it's not the ignitor.

Does this water heater have a control box on the front (with the on/off switch) that says "Honeywell" with about 6 or 7 wires coming off the bottom?
 
  #3  
Old 09-01-08, 07:44 PM
P
Member
Thread Starter
Join Date: Aug 2008
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
No...there are 7 wires coming out of a box that says Robert Shaw on it. Also, now it won't fire at all. When I reset it, the ignitor glows but won't fire, like it's not getting any gas.
 
  #4  
Old 09-05-08, 03:05 PM
P
Member
Thread Starter
Join Date: Aug 2008
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
It's solved. It was the valve which has been replaced.
 
  #5  
Old 09-05-08, 11:43 PM
H
Member
Join Date: Jul 2005
Location: New York
Posts: 657
Upvotes: 0
Received 0 Upvotes on 0 Posts
Glad you're ok now. I was suspecting it was the valve. These integrated gas valves can be problematic at times.
 
 