Can't seem to fix my lower element!


  #1  
Old 10-02-12, 10:10 AM
R
Member
Thread Starter
Join Date: Jan 2011
Location: USA
Posts: 34
Upvotes: 0
Received 0 Upvotes on 0 Posts
Can't seem to fix my lower element!

At a loss with this one. I have an electric hot water heater, where the lower element is not functioning. Below are the steps I've gone through, but the lower element still doesn't heat.

- Ran voltage tests with a multi-meter, no issues
- Replaced upper & lower thermostats
- Replaced upper & lower elements

I really don't know what else to try at this point. Is it possible my system is wired to only heat half the tank? That's all I can think of at this point that could be wrong.
 
  #2  
Old 10-02-12, 04:25 PM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 36,607
Upvotes: 0
Received 11 Upvotes on 10 Posts
What gives you the impression the lower unit is not operating? If you are having no issues with voltage and you filled the tank with water before you went hot, then the lower unit should be heating. When you removed the lower element was it burned?
 
  #3  
Old 10-02-12, 05:11 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 15,997
Received 85 Upvotes on 77 Posts
Both elements do not come on at the same time. Its either one or the other. Lower the temp on the upper and raise the temp on the lower. Then check voltage.

Remember....HIGH VOLTAGE. You can be killed.
 
  #4  
Old 10-02-12, 07:02 PM
R
Member
Thread Starter
Join Date: Jan 2011
Location: USA
Posts: 34
Upvotes: 0
Received 0 Upvotes on 0 Posts
I open the drain valve after it's sat for hours and it shoots out cold water. I also run out of hot water faster than I think I would, which got me investigating to begin with.

Tonight I compared the wiring of the unit, to a wiring diagram I found online I did find some problems, and adjusted to match the diagram. I tested the water about 30 minutes later (still cold), but I'm going to wait. I do see 240v going across the lower element, so I'm hopeful I've fixed the problem.

Thanks!
 
  #5  
Old 10-02-12, 07:31 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 15,997
Received 85 Upvotes on 77 Posts
Did you turn the electric on with no water in it? Even though you have 240v the element may be fried. You need to do a continuity test, or use a clamp on ohm meter to test.
 
  #6  
Old 10-02-12, 08:14 PM
R
Member
Thread Starter
Join Date: Jan 2011
Location: USA
Posts: 34
Upvotes: 0
Received 0 Upvotes on 0 Posts
Water was in the tank when I turned on the electricity (remember the top element heats fine)

I also just ran a continuity test across the lower element (wires unhooked!) and it passed.

I've attached the wiring of my thermostats, if anyone wants to take a look. Forgive me in advance for the nasty wirenut, in order to match the diagram I posted earlier I had to extend the wire.

Thanks for your help guys!