Water heater overflow running


  #1  
Old 01-13-16, 06:15 AM
Rich W Kraemer's Avatar
Member
Thread Starter
Join Date: Jan 2016
Location: USA
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Exclamation Water heater overflow running

The pressure release valve on my water heater runs almost constantly. The only time it isn't open is if I am using the hot water, and for a few minutes afterwards. The tank is only a year and a half old, as is the expansion tank. Ive turned the temperature, and checked my water pressure (it's somewhere between 60 and 70psi) and the new valve said it was rated for up to 150psi and 200 degrees. Not sure what else I can do to stop this from happening.
Please help!!
 
  #2  
Old 01-13-16, 09:14 AM
P
Group Moderator
Join Date: Mar 2003
Location: NC, USA
Posts: 25,971
Received 1,772 Upvotes on 1,584 Posts
You said "new valve"... does that mean you have already tried replacing the valve? You said you checked the water pressure turned down the thermostat but have you checked the water temp? Actually check the water's temp or have you noticed that the hot water is scalding hot?
 
  #3  
Old 01-13-16, 12:49 PM
Rich W Kraemer's Avatar
Member
Thread Starter
Join Date: Jan 2016
Location: USA
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Yes, I replaced the valve once already. I haven't checked the temperature of the water itself, but I wouldn't say it scalding. Especially after turning it down, it's barely hot. Not I'd say very warm.
 
  #4  
Old 01-13-16, 03:26 PM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,355
Upvotes: 0
Received 251 Upvotes on 231 Posts
The expansion tank may have lost its air cushion, perhaps someone let the air out as a prank, or the pressure tank was not pressurized adequately to begin with.

TUrn off the water, open a hot faucet upstairs, and set the expansion tank to slightly less than the normal water system pressure.
 
 