Hot water circulating system mystery

My home was built with two 50-gal water heaters plumbed in series, with a circulating system using a Grundfos 59896115 pump. The water heater with the fresh water feed (and expansion tank) sprung a leak. I had it replaced with a new water heater but now the circulating system isn't working.
The pump runs but no instant hot water inside the house.
I isolated and removed the pump. The impeller spins and i got water flow when I opened the gate valve on the return line.
It's a mystery.
Anybody have any ideas?

Thanks.
 
  #2  
Old 07-25-16, 03:59 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 65,775
Received 4,122 Upvotes on 3,702 Posts
We would need a few pictures of your setup there to comment. http://www.doityourself.com/forum/el...-pictures.html
 
  #3  
Old 07-25-16, 05:22 PM
T
Member
Thread Starter
Join Date: Jul 2016
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Re: Pix

Thanks Pete. Will have them up tomorrow.

Tom
 
  #4  
Old 07-26-16, 12:00 PM
T
Member
Thread Starter
Join Date: Jul 2016
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Pix of this project

Name:  Both Tanks.jpg
Views: 392
Size:  29.5 KBName:  New tank and circ pump.jpg
Views: 402
Size:  28.1 KB

This is what the set-up looks like. Fresh water feeds the new tank which feeds the second tank.

The recirc return feeds back into the new tank.

The Grundfos pump works but no water circulates through the system.

If I turn the system on, the Grundfos pump gets too hot to touch in about 10-minutes.

I'm baffled...

Tom
 
Attached Images   
  #5  
Old 07-26-16, 12:40 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 15,993
Received 85 Upvotes on 77 Posts
Are both valves open before and after the pump? Gate valves often break and when they do its usually in the closed position... Do any of the handles just keep turning and turning?

It appears you have a return on the hot water line from say a master bath?

There should be a check valve somewhere also.. If these stick open then cold water feeds back through the recirc line and youll have no instant HW... Ifact you may have minimal HW everywhere...
 
  #6  
Old 07-26-16, 01:23 PM
T
Member
Thread Starter
Join Date: Jul 2016
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Update

Name:  Check Valve.jpg
Views: 512
Size:  40.3 KBName:  Check Valve-2.jpg
Views: 451
Size:  35.2 KB

New discovery! The check-valve in attached to the water heater. And, the water flows from the bottom of the tank up through the Grundfos into the house. I thought the water returned through the Grundfos into the bottom of the tank.

Either that or, the check valve is installed upside down...

As you can see, the Grundfos got so hot it melted the insulation to the pipes.

Is this any help?
 
  #7  
Old 07-26-16, 01:38 PM
T
Member
Thread Starter
Join Date: Jul 2016
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Update Part Deux

I confirmed the flow arrow on the pump; the check valve is upside down.

Problem solved.

Thank you for your help. Without it I wouldn't have discovered the problem and the logical solution.

Best to you,

Tom
 

Last edited by TCaruthers; 07-26-16 at 01:39 PM. Reason: spelling
  #8  
Old 07-26-16, 02:36 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 15,993
Received 85 Upvotes on 77 Posts
Wow!!! It was that easy???? LOL...

Yes the pump flow is toward the heater.

Hmmm... who installed check valve upside down?


Im glad that may be your issue and post back your final results please... It will help others immensely im sure...
 
 