Hi, I've used a multimeter to determine the lower element is bad. I was just going to replace it, but I noticed one of the wires to the lower element look charred. Could the element going bad cause this or is it something else? All the other wiring on this unit looks fine. The water heater is 5 to 7 years old. The house it is in is much older. And this hot water heater is only on a 20A circuit breaker.
#2
Welcome to the forums.
Usually the insulation chars when the screws on the elements are not tight.
As far as a 20A circuit.... that's a problem. A 4500 watt element uses around 19A of power.
That water should be wired with #10 wire on a 30A breaker.
Usually the insulation chars when the screws on the elements are not tight.
As far as a 20A circuit.... that's a problem. A 4500 watt element uses around 19A of power.
That water should be wired with #10 wire on a 30A breaker.
#3
Member
Thread Starter
Join Date: Oct 2016
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thank you. The charring still has me a little concerned, the screw is as tight as it will go. I will have an electrician install the 30A breaker soon. I will swap the element myself to save a few bucks.
#4
I will have an electrician install the 30A breaker soon.
That water should be wired with #10 wire on a 30A breaker.