Shallow well pump - HELP !
#1
Member
Thread Starter
Join Date: Aug 2005
Posts: 17
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Shallow well pump - HELP !
I just put in a new 1/2 hp shallow well pump. The pump kicks on & off & back on quickly before running. It seems as though the pressure is dropping steadly to about 30lbs then very quickly drops to 20lb & the pump kicks on. The pressure jumps back to 40 & the pump shuts off then quickly back to 20 & back on where it runs fine. Anyone have any ideas on why it would do this ?
#5
Since I have never heard of a well saver tank. Is it a bladder tank or a galvanized pneumatic tank? Or does it have more than one plumbing fitting on it? And does it have a little schrader valve that you can add air to?
If it's a bladder tank, you may have the pressure in the tank set too high and sometimes the bladder will be stuck to the bottom of the tank. Although I think all the manufacturers have gotten past that problem.
bob...
If it's a bladder tank, you may have the pressure in the tank set too high and sometimes the bladder will be stuck to the bottom of the tank. Although I think all the manufacturers have gotten past that problem.
bob...
#7
Ok, that explains it. YOu have too much air in the tank for your switch setting. If you have a 20/40 switch, you need to turn off the pump, open a faucet until the water stops flowing. Let the air pressure in the tank down to 18 lbs. Turn the pump back on. Now it will function properly.
bob...