2" deep well drop pipe size?
#1
Member
Thread Starter
Join Date: Aug 2008
Posts: 4
Received 0 Votes
on
0 Posts
2" deep well drop pipe size?
I have all the parts needed for my 2" deep well. I have my 2" deep well packer and right angle well adapter for the top of the 2" pipe. Right angle adapter will be connected with PVC to the 1HP jet pump, not directly to the adapter.. My question is: I read and called several well companies and they tell me to use 1 1/4" drop pipe or suction pipe. The problem is, the turned couplings to join the pipe together will go inside the 2" pvc pipe but there isn't much room for the water to flow passed them down the 2" casing. I am worried it will not create enough flow or pressure down inside the pipe around the couplings to the packer to help push water up the 1 1/4" pipe. Should I use 1" pipe or will this work ok? I am afraid 1" pipe will not be enough flow. For details about the well,, from top of 2" pipe to water level is 50', well is 140'. Planning on putting packer with foot valve to around 70' to 75'. Just using this well for the lawn and garden. Thanks!
#3
Member
Thread Starter
Join Date: Aug 2008
Posts: 4
Received 0 Votes
on
0 Posts
So couplings are no problem?
Thanks Waterwelldude for the fast reply! So the couplings in the well will be ok for the 1 1/4" even though there very close to the 2" casing? I wasn't sure how much water needed to be pushed down the well for it to perform correctly. I would say when I tried out the coupling inside the pipe, you might could get a credit card to slide by it. Is that enough gap for the water to go by all those couplings as I will add 10' at a time? I already bought the 1 1/4" pipe and couplings today but can return them for smaller if you think it is best to go to 1". I just know how hard it is to pull a leather packer back out! If all is ok, will head back for more 1 1/4" to drop down deeper as you advised. Thanks again.
#5
Member
Thread Starter
Join Date: Aug 2008
Posts: 4
Received 0 Votes
on
0 Posts
Yes, I had an extra 2" pvc pipe and they all fit inside, has a little play, not much, just a little wiggle! But they will all slip inside the pipe and out easy. When the water is pumping, does it pump the same amount down the 2" pipe as comes out the 1 1/4" pipe? Sorry for all the questions, just not very familiar with the 2" well, only worked on the 6-8" drilled wells that uses 2 lines or a submersible pump!
#6
only worked on the 6-8" drilled wells that uses 2 lines or a submersible pump!
I can't think of a submersible pump that uses 2 lines. Do you mean 2 pipes, 2 wires or?
When you are setting the pipe,make sure you don't get any trash in the pipe. Sticks, grass, or any thing else. Keep the drop pipe as clean as possible.

I can't think of a submersible pump that uses 2 lines. Do you mean 2 pipes, 2 wires or?
When you are setting the pipe,make sure you don't get any trash in the pipe. Sticks, grass, or any thing else. Keep the drop pipe as clean as possible.

#9
Member
Thread Starter
Join Date: Aug 2008
Posts: 4
Received 0 Votes
on
0 Posts


#10
Member
Join Date: May 2009
Posts: 1
Received 0 Votes
on
0 Posts
help
I live in Florida I have a f & w 1/2 hp well pump, I think its about a 50 ft 3" well. I have the deep well hook-up from the pump inside the house to the well head its about 20 feet away. The well primes fine, and has adequate pressure. But the suction pipe going from the pump to the well head is only 3/4" pvc instead of 1 1/4" pvc. The pressure line is also 3/4" pvc instead of 1" pvc. F&W recommends at 20 ft away from the well head to the pump to use the larger size pipe for the suction and pressure. The pump is rated @ 30/50 cut-in and cut-off, I have it set to 20/40. Otherwise it continues to run. My question is, Could the smaller diameter pipe between the pump and the well head be causing the lower pressure or is it strictly a weak well and that is why someone used the smaller diameter pipe?
#11
Member
Join Date: Oct 2001
Location: So. Cal
Posts: 1,049
Received 0 Votes
on
0 Posts
The reason F&W (and all the other manufacturers) recommend the bigger pipe is because of friction losses. Friction loss = pressure loss. As water runs through piping, it creates friction, which means the pump has to create more pressure to overcome the loss. This happens on both the suction side and discharge side of the pump. The smaller the pipe, the more friction loss there is.
If the pump is to be installed away from the well, the piping size should actually be increased to alleviate the friction loss.
I don't know the reason your pipe size was decreased, but perhaps the pump was "overpumping" the well, which can happen. Without knowing the capabilities of the well, I can't say that increasing pipe size would help anything, but I also don't think it would hurt a thing.
Ron
If the pump is to be installed away from the well, the piping size should actually be increased to alleviate the friction loss.
I don't know the reason your pipe size was decreased, but perhaps the pump was "overpumping" the well, which can happen. Without knowing the capabilities of the well, I can't say that increasing pipe size would help anything, but I also don't think it would hurt a thing.
Ron