I just installed Basement Watchdog Sump pump. I got below from the manual.

It said that "When a check valve is used, a 1/8 in. (3.2mm) air bleed hole must be drilled in the PVC pipe above the pump. Drill the hole at a 45° angle
toward the bottom of the sump to avoid splashing water outside the sump
pit.
"
Name:  Sump Pump 45 angle Info.jpg
Views: 30882
Size:  53.7 KB

So my question is which angle I should drill the hole; opt1 or opt2?

Name:  Sump Pump 45 angle drill.jpg
Views: 13693
Size:  24.9 KB

Thank you for helps.
 
  #2  
Old 01-31-13, 08:11 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes on 30 Posts
Option two. You want the water from this vent to go back in the sump. Ideally you would add an 1/8 inch pipe fitting and run copper tubing back to the sump.
 
  #3  
Old 01-31-13, 08:29 PM
F
Member
Thread Starter
Join Date: Oct 2012
Location: USA
Posts: 18
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thank you Furd. That is what I thought. If I go Opt1, it will have water jet comes out from the hole when pumping water.

I like your idea to have 1/8" pipe. But how? Can you post a picture please?

Thanks.
 
  #4  
Old 02-01-13, 08:59 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes on 30 Posts
No picture but it is easier than it sounds. Drill the hole with a 5/16 inch bit and tap it with an 1/8 inch pipe tap. Don't run the tap all the way in so as to have the fitting "jam up" sooner. Get a brass 90 degree tubing fitting; 1/8 inch on one side and 1/4 inch tubing on the other. Screw the fitting into the tapped hole and point the tubing connection down. Add some tubing and you're done.

I don't like an 1/8 inch vent as it is too easily plugged by debris. !/4 inch is not too large. As long as the vent hole is below the sump cover you don't really need the tubing going down.
 
 