which float switch

Looking to set up a system, 220v deep well pump fills water tank which gravity feeds house. The main power circuit to power the well pump has inline 2pole contactor switch with is energized by a 120v circuit which runs through a float switch in the water tank. When water level drops the float switch falls, completing the 120v circuit, then throwing the contactor switch and energizing the pump circuit.

which float switch do I need for this. I like the look of the switches that go through the upper bulkhead fill fitting on the water tank, with the threaded bushing, this way the tank can be capped and sealed for sanitation purposes.

I don't know much about the technical terms of the switches so could use some help.
thanks
 
  #2  
Old 09-17-14, 10:59 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,054
Received 3,420 Upvotes on 3,066 Posts
This should be in the same thread you already started.

Normally you would use two floats. One to start the pump and one to stop it. If you use a single float then usually you only have a less than a foot between pump on and off.
 
  #3  
Old 09-18-14, 08:56 AM
L
Member
Thread Starter
Join Date: Sep 2014
Location: USA
Posts: 8
Upvotes: 0
Received 0 Upvotes on 0 Posts
Ok sorry bout new post didn't think about it.

Which specific switches would you recommend? Do you have a link to a diagram of how to set this up? Thanks for your help
 
  #4  
Old 09-18-14, 09:35 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,054
Received 3,420 Upvotes on 3,066 Posts
In the following link.... look for the Wide Angle Float Switch - pump UP type. Just below that is a chart that tells you where to tether the float for the anticipated amount of water height movement.

This float will allow you to control the tank wit a single float. It comes with a piggyback which you could off if not needed. This company is also out in Cal. with you.

Plumbing supply company/alarm.html
 
  #5  
Old 09-18-14, 10:34 PM
L
Member
Thread Starter
Join Date: Sep 2014
Location: USA
Posts: 8
Upvotes: 0
Received 0 Upvotes on 0 Posts
10-4 thanks..................
 
  #6  
Old 09-24-14, 10:46 PM
L
Member
Thread Starter
Join Date: Sep 2014
Location: USA
Posts: 8
Upvotes: 0
Received 0 Upvotes on 0 Posts
One more thing here, when calulating for wire size what is the load rating of a contactor hooked to a float switch? Or what size wire for a 650' run from the contactor to the float switch?
 
  #7  
Old 09-24-14, 11:42 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,054
Received 3,420 Upvotes on 3,066 Posts
There is very little voltage drop as the contactor coil doesn't present much load.
#12 wire would probably work fine.
 
  #8  
Old 09-25-14, 09:40 AM
L
Member
Thread Starter
Join Date: Sep 2014
Location: USA
Posts: 8
Upvotes: 0
Received 0 Upvotes on 0 Posts
I found 18-2 sprinkler control direct bury wire rated to 600v, I found a amp rating to throw contactor and did volt drop calc, I think it should work and be way cheaper then 12g wore with no splices. Ill let y'all know how it works, thanks for the help
 
 