Sewage pump circuit size
#1
Member
Thread Starter
Join Date: May 2014
Location: United States
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Sewage pump circuit size
I'm going to upgrade my sump pump to a sewage pump to deal with a high water table issue. The sewage pump (liberty LE51A) is 1/2 HP with a Full Load Amp of 12A and a Locked Rotor Amp of 22A. My question is can I use the existing 15A dedicated circuit that my current pump uses or do I need to put in a 30A circuit? I don't want make sure I don't trip the breaker when the pump starts.
Thanks
Thanks
#2
If you need to stay with the 120v pump then I'd recommend running a #12 line with a 20A breaker. The load of that pump is close to tripping the 15A breaker.
If it was me.... I'd upgrade to a 240v pump.
Liberty LE52A is 1/2HP 208/230v full load 6.8A and locked rotor of 12A.
You could use the existing 15A dedicated circuit and convert it to 240vac with the addition of a 2P15A circuit breaker. The biggest improvement in using a high draw pump on 240v instead of 120v is that your lights won't blink as much when the pump starts.
If it was me.... I'd upgrade to a 240v pump.
Liberty LE52A is 1/2HP 208/230v full load 6.8A and locked rotor of 12A.
You could use the existing 15A dedicated circuit and convert it to 240vac with the addition of a 2P15A circuit breaker. The biggest improvement in using a high draw pump on 240v instead of 120v is that your lights won't blink as much when the pump starts.
#3
Member
we generally use zoeller's m53 pumps which take 12a to start,,, why bother w/effluent pump ? IF the pump's outside, according to nec it needs a dedicated 20a circuit,,, inside,15a's fine but we do this for a living

#5
If you are doing the electrical work yourself.... feel free to ask questions on the install.
I can tell you something now to consider..... install a two pole disconnect at the pump location if it's a hardwired pump. If the pump plugs in.... that is your service disconnect.
I can tell you something now to consider..... install a two pole disconnect at the pump location if it's a hardwired pump. If the pump plugs in.... that is your service disconnect.
#6
Member
if you have that much wtr to cause you to consider 230v pump, you're MUCH better served having 2 m53 pumps imo
even if it requires another sump & discharge line
we would NEVER recommend what you're doing to a client nor, imo, would any other bsmt wtrproofing co