What Does a Hot Ground Reverse Reading Mean?
2 hours
Advanced
- 45
“Hot and ground reversed” is only one of the many diagnostic readings that can be indicated by an outlet/receptacle tester (Figure 1). It usually indicates the absence or malfunction of a neutral conductor somewhere in your system.
If you receive a Hot/Grd. Reverse reading, check your neutral conductors. One of them might be burned out, requiring replacement, or simply loose, in need of a gentle tightening.
A few different kinds of situation can trigger such a reading, however. To get a more complete picture of receptacle test results, check out the info below.
The tester is simply an instrument that reads the relationship between the hot, the neutral, and the ground wires at specific receptacles within a circuit and a miswired receptacle will not necessarily be reflected into all the other outlets within that circuit.
When the "correct" reading isn't shown by the proper lights sequence on the receptacle tester, the lights that do come on will indicate the probable cause relative to the faulty wiring, caused by broken or mixed-up wires, or wires attached to wrong terminal screws. The fault, however, might be at a different location within that circuit and some tracking could be required along the line to find its origin. While doing electrical work, there’s also the possibility that a combination of multiple faults results in misdiagnosis. The following is a progressive write-up describing every possible diagnosis and all their possible causes.
Figure 2 describes all the outlets in the following circuits, showing two outlets, each with three openings—one short slot connected to the hot terminal, one longer slot connected to the neutral terminal (providing the return path), and the semi-circular ground opening matched to the green ground terminal but also connected to the metallic enclosure box.
1. Open Ground (Gnd)
Figure 3 shows two circuits with the same problem but in different locations. Although the flaw is practically unnoticeable without a tester, a break (or a loose connection) in the ground wire at either location does not prevent an appliance from working when plugged into it, but it does create a serious electrocution hazard from outlets #2 in circuit A and from both receptacles in circuit B should a short circuit occur while the open ground situation exists.
An “Open Ground” reading is often the result of someone forgetting to connect the wire to the green terminal screw, or a broken ground wire, causing the following results—
1.1—A multimeter not showing any voltage between the Hot and the Ground terminals at outlet #2 of circuit A and at neither outlet in circuit B but reading 120 Volts at outlet #1 in circuit A.
1.2—The multimeter showing 120 volts between the Hot and the white Neutral connectors on all the outlets.
1.3—An outlet tester’s lights showing “Open Ground” on outlets #2 in circuit A and both outlets in circuit B, and “Correct Wiring” when plugged into Outlet #1 in circuit A.
A word of caution—A physical connection must also ground the enclosure box to the receptacle’s ground terminal.
2. Open Neutral
In Figure 4, circuit C has power in outlet #1 but none at outlet #2 nor is there any power at all in circuit D. Check for a broken or loose wire connection on one of the white leads at the specified points (inside the red star) in circuits C and D.
Testing the receptacles will result in one of the following:
2.1—No voltage showing between the Hot and the Neutral terminals in either outlets #1 or #2 of circuit D or outlet #2 of circuit C, but the multimeter would read 120 volts at outlet #1 in circuit C.
2.2—A 120 Volts reading between the Hot and the ground at any of the outlets of both circuits C and D.
2.3—A 120 Volts reading between the Hot and the Neutral at outlet # 1 of circuit C only.
2.4—The outlet tester showing an “Open Neutral” on outlets #1 in circuit D as well as in outlets #2 in both circuits C and D, and “Correct Wiring” when plugged into outlet #1 in circuit C.
Note: An appliance would work on outlet #1 in circuit C but not on any of the other outlets.
2.5—In one special case, “Open Neutral” can easily become a “Hot and Ground Reversed” as highlighted in section “5—Hot & Gnd Rev”.
3. Open Hot
With no lights on the tester at outlet #2 in circuit E or anywhere in circuit F, except for outlet #1 in circuit E that tests “Correct”, the Hot wire is open past the last outlet that lights it up—it could even be on the outfeed wire of that outlet—or before outlet #1 of circuit F (Figure 5).
4. Hot & Neutral Reversed
Figure 6 shows two circuits with an unconventional mix up of wires at some outlets. This frequently happens when adding receptacles to existing circuits, and it DOES provide voltage (although unsafe) to all the receptacles, along with the following results—
4.1—The receptacle tester will only show “Correct wiring” on outlets # 3 of circuit G and outlets # 1 & 4 of circuit H.
4.2—A multimeter will show 120 Volts across the Hot and the Neutral terminals of ALL the outlets.
4.3—A multimeter will show 120 volts between the Hot and the Gnd terminals on outlet #3 in circuit G and outlets #1 & 4 in circuit H.
4.4—The multimeter will not show any voltage between the Hot and the Gnd terminals on outlets #1 & 2 of circuit G and outlets #2 & 3 of circuit H, but 120 Volts between the Neutral and Gnd terminals making these outlets lethally hazardous by placing a live voltage on every grounded part of all appliances plugged into it.
5. Hot & Ground Reverse
This contradicting statement implies that the ground wire is energized with 120 volts while the hot wire is grounded, which would create a short circuit! But as illustrated in Figure 7, there are some wiring configurations that, without shorting out, can cause the receptacle tester to give a “Hot & Gnd reverse” result.
5.1—Such a situation could occur as in Figure 8, with an open neutral line upstream of the faulty receptacle (towards the panel) while a load such as a lamp was plugged into that receptacle or another receptacle downstream (farther down the line). The open line would prevent the current from flowing, keeping the light bulb from lighting. The light, therefore, can’t cause a voltage drop, but does create an interconnection between the hot and the neutral slots of the outlet energizing the two of them at 120 volts, which the receptacle tester identifies as “Hot & Ground Reverse.”
5.2—A “bootleg” ground situation is often present in older installations before safer electrical installations that included a ground wire existed. With the absence of the ground wire within the circuit, the receptacle’s ground terminal is connected to the neutral—which is a code violation. A standard receptacle tester cannot detect a Bootleg ground reporting it as correctly wired or “correct”.
The practice is unsafe and less dangerous, however than the “reverse bootleg”, where the hot and the neutral wires get mixed up ending up on the wrong terminals with the ground terminal connected to the Hot instead of the neutral wire (Figure 7) and creating the same hazard as described in section 4.4.
So armed with all this info and a receptacle tester, you’re now ready to make your home a safer place.
Hot Ground Reverse Reading FAQ
What does hot and ground mean?
Electrical wiring is actually color-coded, which makes things much easier when you're trying to install a new electrical fixture. Black wires are "hot," which means they are carrying electricity from the breaker panel to the light, appliance, or whatever is receiving power.
The ground wire is a safety wire, providing another path for electricity to flow. The current that is not being used by devices and fixtures flows back to the breaker box through this wire.
When a ground wire is hot, the connection between the hot wire and the ground wire has been reversed or crossed. This means the hot wire is connected where the ground wire should be connected, and the ground is connected when it should actually be the hot instead.
What would cause a ground wire to be hot?
There are several reasons why a ground wire may be "hot," which means it is receiving more electrical voltage than it should. This might indicate improper connections, an electrical leak in the circuit itself, or some kind of damage in the wiring.
Can a bad ground wire cause a fire?
Anything and everything that interrupts the normal flow of electricity in wiring is a potential fire hazard. This includes ground wires that are hot or otherwise experiencing problems.
Faulty wiring can lead to sparks, power surges, and other issues that can, in worst-case scenarios, create sparks that lead to a fire hazard.
How do you know if neutral and ground are reversed?
Reverse polarity in ground wires, also known as hot neutral reversed, indicates that something has been wired incorrectly and this can cause the flow of electricity to move in reverse. This is a serious shock hazard and should be fixed right away.
How do you check for reverse polarity?
If you think you have a problem with reverse polarity, the simplest way to check is to use an outlet tester. This will show you how much voltage the outlet is receiving.
When wired properly and receiving the right amount of electricity, the outlet will test around 110 to 125 volts, on average. If the voltage the outlet is getting does not fall into these parameters, you may have a problem with reverse polarity.